Abs. Error
|
Absolute magnitude of the difference between the PID setpoint and process variable.
|
ADV_PID
|
Advanced PID
|
AI
|
Analog Input
|
ALARM_A
|
Analog alarm
|
ALARM_D
|
Discrete Alarm
|
Algorithm
|
A step-by-step problem-solving procedure, especially an established, recursive computational procedure for solving a problem in a finite number of steps.
|
AO
|
Analog Output
|
Auto mode
|
Enables the device to be commanded from logic.
Note: The mode can be changed while the Controller runs.
|
DC2S
|
Device Control 2 State
|
DC3S
|
Device Control 3 State
|
Debouncing
|
Ensures that only a single signal will be acted upon for a single opening or closing of a contact.
|
DI
|
Discrete Input
|
DO
|
Discrete Output
|
Forced data
|
Overrides the PV value with a user specified value.
|
IND_A
|
HMI Analog Indication
|
IND_D
|
HMI Discrete Indication
|
Inhibition
|
Logic within the control program to suppress faults or alarms automatically.
|
Interlock
|
Prevents the device from running; high temperature interlock for a motor.
|
Local setpoint mode
|
The PID setpoint can be changed from HMI faceplate only.
|
Locked mode
|
The logic has locked the mode into either manual or automatic. It cannot be changed through the faceplate.
|
Lock out
|
The device is being serviced and is unsafe for operation.
|
Magnitude of Error
|
Absolute magnitude of the difference between the PID setpoint and process variable.
|
Manual mode
|
Enables the state transition commands to come from the operator SCADA or Engineering Workstation when online to the Controller.
|
MANUAL_SP
|
HMI Manual Setpoint
|
OP
|
Output.
|
Parallel (Algorithm)
|
PID terms are calculated independently in parallel to one another.
|
PBUTTON
|
HMI Discrete Pushbutton
|
Pct. Error
|
Absolute value of the ratio of the error to the span of the process variable.
(ABS(SP-PV)/PX-PN)*100.0)
|
PID
|
PID
|
PV
|
Process variable.
|
RAMPSOAK
|
Ramp Soak Setpoint Generator.
|
Remote setpoint mode
|
The PID setpoint is generated in logic and cannot be changed in the faceplate.
|
ROC
|
Rate of change.
|
Selectable mode
|
The mode (manual or auto) can be changed through the faceplate.
|
Series (Algorithm)
|
The PID terms are dependent on one another and combined in series.
|
SP
|
PID setpoint
|
Suppressed
|
The user suppresses the alarm generation within the HMI system.
|
TOTALIZE
|
Totalized Flow Rate
|